Cable Sizing Verification in Italian Software
[1] Cable Sizing Verification in Italian Software
Messaggioda Foto UtenteSelk » 5 set 2019, 7:10
This is regarding cable sizing and protective device selection in a switchboard. Kindly help me out to understand the basics in the attached schedule which is made in a Italian software https://www.exel.it/ (Progetta Integra) and that is the reason I'm here.
1) What is Id?
2) What is Igt end of line?
3) What is I2t start of line? Why is it calculated only for Phase conductor? Is it mean the cable impedance is calculated for the first few metres of the cable from the switchboard? Can you give some example? I can easily arrive at the value of K^2S^2 by multiplying XLPE copper, K =143 and the S= Cross section area of the conductor.
4) What is I2t end of line? Why is it calculated for neutral conductor?
5) What does Lmax mean? Is it the maximum length that is permitted for a particular cable size to not to exceed the allowable voltage drop?
How are the values for the above parameters arrived at in the attached schedule? can anybody give inpus
Your inputs are much appreciated!
Switchboard Schedule_Questions.pdf
(53.8 KiB) Scaricato 149 volte
Foto UtenteSelk
[2] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utentemarco76 » 5 set 2019, 8:45
Hi, the I2t or Joule integral is a measure of the thermal stress or thermal energy let through by the fuse during short circuit interruption. You might have a failure at the end or at the beginning of your cable.
Foto Utentemarco76
1.253 2 5
[3] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utenteesisnc » 5 set 2019, 8:52
1) Nominal current of differential protection relay : Id = 0,03 A or 30 mA
2) In reference to standard CEI 64-8 (IEC 60364) section 533.3 :
Igt = I (short circuit end of line), in this case phase-neutral Isc
Isc = 0,8 Uo/(1,5 r 2 L/S) = 421,3 A
Uo = 231 V (nominal phase-neutral volt)
r = copper resistivity @ 20°C 0,0172 (Ohm x sq mm/m)
L = simple line length (85 m)
S = copper line cross section (10 sq mm)
Foto Utenteesisnc
4.405 2 9 11
[4] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utentemarco76 » 5 set 2019, 8:52
Id is the differential current or residual current of RCD (residual current device).
Ultima modifica di Foto Utentemarco76 il 5 set 2019, 9:08, modificato 1 volta in totale.
Foto Utentemarco76
1.253 2 5
[5] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utentemarco76 » 5 set 2019, 8:54
In case you have a smaller cross-section for the neutral conductor
Foto Utentemarco76
1.253 2 5
[6] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utentemarco76 » 5 set 2019, 8:57
Maybe the maximal cable lenght, that the fuse can protect
No, I think you were right
Foto Utentemarco76
1.253 2 5
[7] Re: Cable Sizing Verification in Italian Software
Messaggioda Foto Utenteshizuto » 5 set 2019, 12:33
Hi Selk
I know very well Progetto INTEGRA, so:
1) What is Id?
It is the RCD current (with Type of RCD)
It is Current fault between Phase and PE
i2t is not calculated, but it is read on let trough energy curve, by intersection with correspondant fault current. Usually (but not always), i2t at start of line is the maximum value, and it is compared with K2S2 (calculated).
at the start of line, there is a value of Ik(max), that corresponding a i2t value read on curve; at the end of line, ther is another value of Ik(min) and related i2t, but I think it was a mistake the text "End of line".
Exactly
Foto Utenteshizuto
0 1